Author Topic: Same conductor size in different power cords have different Amp ratings.  (Read 303 times)
0 Members and 1 Guest are viewing this topic.
Opcom
Patrick J. / KD5OEI
Contributing
Member
*
Offline Offline

Posts: 8345



WWW
« on: May 10, 2025, 01:32:38 AM »

I'm trying to understand how a smaller gauge of power cable handles a higher current.
The two cable types below are both 4-conductor, so as for 120/240V and GND, as in  reguar USA 240V household juice.

Type "SOOW". It needs to have 4-gauge conductors to handle 60 Amps. The typical big black cable.

Type "W". It only has to have 8-gauge conductors to handle 65 Amps. No idea what it looks like. Looking up the same thing in 4-gauge size, that is rated 114 Amps!

How does one handle 60A with 4 Gauge conductors, and the other can handle 65A with the smaller 6 gauge conductors? It does not make any sense.
Logged

Radio Candelstein
KD6VXI
Contributing
Member
*
Online Online

Posts: 2740


Making AM GREAT Again!


« Reply #1 on: May 10, 2025, 06:01:31 AM »

The conductors are rated for different temperatures.

This is where we, as electricians, have to do yhr math on what we are connecting to.

Not to mention, SOOW cord is temporary only.

At least, code says it is.  Couldn't tell you how many power cords I've made out of SOOW.

I rate SOOW the same way as THHN.  8 gauge is 45 amps.

--Shane
WP2ASS / ex KD6VXI
Logged
W1RKW
Contributing
Member
*
Offline Offline

Posts: 4475



« Reply #2 on: May 10, 2025, 04:05:40 PM »

isn't the conductor temperature rating dictated by the insulation type, thickness and spacing and how it can pass or radiate heat?
Logged

Bob
W1RKW
Home of GORT.
KD6VXI
Contributing
Member
*
Online Online

Posts: 2740


Making AM GREAT Again!


« Reply #3 on: May 10, 2025, 07:46:13 PM »

Yes.

As well as limited by the device it's connected to.

IE, if you have 90c rated wire and 75c rated breakers (or switches, outlets, what have you) then the engineer (electrician) is required to do a thermal calc on the wire to limit current to a value that won't allow the wire to reach a temp over the connections rating.

It's usually easier to just upside the wire.

--Shane
WP2ASS / ex KD6VXI
Logged
Opcom
Patrick J. / KD5OEI
Contributing
Member
*
Offline Offline

Posts: 8345



WWW
« Reply #4 on: Today at 01:20:29 AM »

Very interesting! Yall gave me a lot to think about and to research. The reason I'd broached the subject is that a detachable power cord about 20FT long has to be made up and I hadn't made up a power cord this large Amp-wise. - so I explored all the different kinds of flexible 4-conductor wire. The more flexible the better.

From what was said, the temperature rise depends on many more factors than the wire size.  Maybe it's nit-picking because an 8 gauge will only drop 1.5V at 60A (90W), and the 4 ga. drops 0.7V (28W). I probably want to stick to the larger wire sizes just to keep temperatures down especially at terminations and contacts.  Inside the equipment, the big wiring is #6 THNN but those are single stranded conductors

=====
learned some stuff on the type S and type W power cords, just to compare the two in the same gauge:

The 4 GA type W is $10/FT., EP rubber insulation, jacket OD=1.245", strands:259.  
-More flexibe because of more strands or the rubber? who knows. Maybe more durable since it's for mining.

4/4 SOOW on the other hand is but $7.12/FT., EPDM insulation, jacket=1.00, strands: 119/25

=====
The 60 amp  connectors for this:
A Hubbell 460B12W is the chassis-mount power inlet, and a 460C12W (these are rating 75 deg C) is the connector on the end of the power cord which will plug into that. I aready have these connectors. The far (wall) end of the power cord will probably be a standard 60A dryer plug and receptacle. -so that is def a limiting factor in the wire size of the cord,

There are industrial Hubbell type of these same connectors but reversed polarity for the 'wall' end of the power cord, but all of these connectors are obscenely expensive. I got some cheap by trading and from ebay.

The inexpensive residential dryer receptacle and plug exist only for the 'wall' end of the cord. There are no reversed-polarity counterparts that I might have used at the chassis (and dryers have no detachable power cords), soo... had to go to an industrial connector set at the equipment if I wanted a detachable power cord.


some links to the wire, but I'm not sure now if that large a size is needed.
https://www.wireandcableyourway.com/4-awg-4c-type-w-portable-power-cable

https://www.wireandcableyourway.com/4-4-soow-portable-cord-600v-non-ul

and this guy's page is interesting.
https://forums.mikeholt.com/threads/what-is-the-ampacity-for-8-awg-wire-50-or-40.37254/

All this is a learning curve.


* HUBBELL 460 CONNECTOR SET.png (242.29 KB, 691x404 - viewed 0 times.)
Logged

Radio Candelstein
KD6VXI
Contributing
Member
*
Online Online

Posts: 2740


Making AM GREAT Again!


« Reply #5 on: Today at 07:06:35 AM »

Is this for the 3cx3000?

If so, do you REALLY need 60A?

60A is 6 gauge.  I wouldn't do 8.

I have done 8 on a 3000 before. 

Remember peak current draw isnt the same.  Plan on peak current draw for your wire size.

--Shane
WP2ASS / ex KD6VXI
Logged